Hostigation DOWN again Because of power maintenance :(

13»

Comments

  • Any A+B solution and facility that offers such should have multiple everything @Maounique.

    As long as they do these PDUs with the A+B feed support will suffice.

  • @miTgiB said: Of course there is, but that doesn't help with the task the DC is performing. I think you need to step back and take a breath, you are not paying for enterprise level service, stop acting as if you did.

    This

  • concerto49concerto49 Member
    edited February 2013

    @pubcrawler said: What was likely to fail @concerto49?

    The ATS PDU will fail and is the single point of failure. As in that thing isn't that reliable compared to a normal PDU and would kill all the servers connected. A+B on the servers is the proper way to do redudant power with separate feeds into separate PDU connected to the server via redudant PSU.

    Any outage on this ATS PDU would kill the entire strip regardless of any A+B.

  • concerto49 said: The ATS PDU will fail and is the single point of failure.

    That's why you don't use the ATS as the power source in a rack. At the day job, all our racks have A/B power with 2 0U PDUs per rack, one for each feed. The ATS, if needed, is wired between the vertical PDUs and is used to power the switch in the rack and older single PSU servers. Racks are cross wired in pairs with all servers using bonded connections going to the switch in its rack plus another to its partner rack switch.

  • And maint done and back, for good I hope