How does power usage work in colocation?

Hi,

Google didn't help much, I'm trying to get a better understanding of how power works in colocation.

For power, for example if the plan is 1A, is that the average or the peak limit? What happens if goes over the limit? Also I have not seen any provider with pay as you go power usage, is this not a thing?

Thanks.

Comments

  • @nameserver said: for example if the plan is 1A, is that the average or the peak limit?

    peak limit

    @nameserver said: What happens if goes over the limit?

    you'll get warning or additional billing or forced to upgrade to higher tier or andrew from legal will sue your arse. or the breaker just trip

    Thanked by 1rpqu
  • AlyxAlyx Member, Host Rep

    Really depends on the provider I think.
    We for example charge per kWh, so basically the "pay as you go" thing you mentioned.

  • @Alyx said:
    Really depends on the provider I think.
    We for example charge per kWh, so basically the "pay as you go" thing you mentioned.

    How do you calculate the kWh usage? Average?

  • AlyxAlyx Member, Host Rep

    @nameserver said:

    @Alyx said:
    Really depends on the provider I think.
    We for example charge per kWh, so basically the "pay as you go" thing you mentioned.

    How do you calculate the kWh usage? Average?

    Pull the data from the metered PDU.

    Thanked by 1tux
  • @Alyx said:

    @nameserver said:

    @Alyx said:
    Really depends on the provider I think.
    We for example charge per kWh, so basically the "pay as you go" thing you mentioned.

    How do you calculate the kWh usage? Average?

    Pull the data from the metered PDU.

    I see. Thanks for answering.

    Thanked by 2Alyx oloke
  • RAVNIXRAVNIX Member, Patron Provider

    In most cases your not supposed to sustain more than 80% continously

    Thanked by 1nameserver
  • In my experience, treat the 1A as a peak / circuit limit rather than an average you can sit at all day. As RAVNIX noted, staying under about 80% sustained is the practical rule, partly because breakers and PDUs are rated for continuous load that way, and partly because a short spike - a server rebooting, fans ramping up, or disks spinning up - can push you over if you are already close to the line.

    What I would check in the contract is whether the 1A is per outlet, per server, or a shared allocation, and whether billing is a flat fee up to that limit or metered by kWh, like Alyx described. Those are quite different: with a flat allocation you pay the same whether you draw 0.3A or 0.9A, while with metered billing your actual draw matters and idle servers still cost something. A metered PDU, or even a cheap plug meter before you commit, is the easiest way to see your real idle and load draw instead of guessing from the PSU rating.

    If you do go over, ScreenReader's list is realistic - a warning, extra billing, or being asked to move to a higher tier. I would rather size for the sustained load with some headroom than plan to run right at 1A.

    Thanked by 1nameserver